This topic seems to be taking a life all it's own. I think it is fitting to give it it's own thread. Let the whipping begin.
To start. I will give you something to chew on.
Reason number 1 why you need more than 2 pipe diameters from the trap weir to the tee in the wall.
Say you have hair,lint,or string in the trap (obviously very common). That foreign matter is laying in the outlet of the trap. If the outlet is within 2 pipe diameters of the drop pipe that foreign matter could be laying from the outlet of the weir and down the drop pipe. The water would be wicked/siphoned out of the trap by the foreign matter.
It does happen. Think about toilet paper in a wcl drapped over the trap. Wicks it out doesn't it:yes:
This is one of the primary reasons for having more than 2 pipe diameters to the drop. What say you?
To start. I will give you something to chew on.
Reason number 1 why you need more than 2 pipe diameters from the trap weir to the tee in the wall.
Say you have hair,lint,or string in the trap (obviously very common). That foreign matter is laying in the outlet of the trap. If the outlet is within 2 pipe diameters of the drop pipe that foreign matter could be laying from the outlet of the weir and down the drop pipe. The water would be wicked/siphoned out of the trap by the foreign matter.