every tool is a hammer
Joined
·
4,304 Posts
Discussion Starter #1
This was in a 6" rpz control valve I tested that failed. Neither valve would hold. So I had the city come out and turn off the water at the b-box. I popped the bonnet on the 6" #1 control valve and this is what was in the seat. This is supposed to be Chicago water, which means Lake Michigan water. The town must be blending it.
 

Attachments

·
Professional Bullshioter
Joined
·
6,092 Posts
Most of the time I remove crushed stone or gravel from the checks. Poor practices on installation.

Guys don't keep the pipe clean in the ditch and then they don't do as the manufacturer requires and flush the line before installing the BFP.

That scale looks like it's right out of the DI main. We get that alot after a service interuption.
 

·
Banned
Joined
·
3,806 Posts
90% of New Lenox does not have Lake Michigan water, at least they didn't five years ago when I repaired the PSV in the Frankfort pumphouse.
 

·
J. McCabe Plumbing Inc.
Joined
·
409 Posts
This is why a wye-strainer should be installed before all control valves, PRV's. RPZ's, Bfp's etc.

Sell them a wye-strainer.
 

·
Illinois Licensed Plumber
Joined
·
4,253 Posts
This is why a wye-strainer should be installed before all control valves, PRV's. RPZ's, Bfp's etc.

Sell them a wye-strainer.
If its on a fire sprinkler they do not want a wye strainer installed.
 