it's great for reno's or if you need to add a line after the fact. I prefer to thread black iron throughout but sometimes it's not practical so I use csst. I see it installed with plastic J-clips(used for pex) a lot and it fails inspection. so check with your code because mine says you need to use metal clips. I think it will stand the test of time and if a nail is put through it... just heat the nail up with your torch until it falls out :whistling2: :no:
 

·
Registered
Joined
·
1,880 Posts
I've used quite a bit of trac ,,, Am VERY happy with it ! Sure a nail can go through it ,, however we learn that as you run it in a vertical wall ,,,, leave it somewhat loose so it can move a little . Otherwise it really is good stuff !!

IMO

Cal
 

·
Plumber Manhattan Beach
Joined
·
828 Posts
I like Trac, especially when I am installing tankless. I do agree, snak it loose in the walls and when the inspector calls you on it, fight him. Inspectors here want to see the book on it, to check for approvals and all.

I don't see any problems with it as long as it does not get hit my lightening or something. (Heard something bad about that somewhere)

electricians need to take a section of wrap off it to properly ground.
 

·
Registered
Joined
·
398 Posts
Inside a house I will run threaded steel (black iron) 99% of the time. The other 1% goes to Copper when I can't run steel. Steel offers several benefits:

1) Durable & tough - can take a beating
2) Reliable & proven
3) Challenging, yet rewarding to install at times (requires some planning in tight installations for wrenching)
4) Common - every supply house will carry fittings & pipe.
5) Safe - you can't put a hole in it (well, unless you're doing something serious but it'd be the last product out there certified for gas use that would give up the ghost).

The only thing that irks me about steel is that a lot of the steel the supply houses carry is made in China. But otherwise I feel a sense of duty and safety when I install it over other products in the houses I work in.
 

·
Master Plumber
Joined
·
1,069 Posts
electricians need to take a section of wrap off it to properly ground.

NOOOOOOOOO!!!!!

Never, ever let an electrician ground to CSST pipe. That's extremely dangerous.

The ground must be to a fitting or to steel pipe that is connected to the CSST. But never to the CSST.
 

·
Certified Lunatic
Joined
·
20,658 Posts

·
Plumbing and Gas SCO
Joined
·
1,437 Posts
I love gastite. You can make it look really good if you try. It cuts install times very well which makes up for the higher cost of materials. In new construction saving time is always a blessing. I am also moving away from the home-run style of installing pex. I am using Uponor flow though manifolds now. Run a 3/4 main through the home and branch where you need to. Put an end manifold on the cold or even tie it back into the main. Run the hot back to the tank for a recirc or just plug it for future. Cuts install times that much more and really looks better than the spaghetti of a home run system.
 

·
Master Plumber
Joined
·
1,069 Posts
A pertinent quote that backs up what I said:

For attachment to the CSST gas piping system, a single bonding clamp must be attached to either a segment
of steel pipe or to a rigid pipe component. The corrugated stainless steel tubing portion of the gas piping
system shall not be used as the point of attachment of the bonding conductor at any location along its length
under any circumstances.
The emphasis was theirs.
 

·
Always Something
Joined
·
1,369 Posts
NOOOOOOOOO!!!!!

Never, ever let an electrician ground to CSST pipe. That's extremely dangerous.

The ground must be to a fitting or to steel pipe that is connected to the CSST. But never to the CSST.

100% correct. Never ......ever bond to the actual CSST. You will cruch / kink the pipe in no time. Trac pipe...is IMO not a great product. I don't care for the fitting design, it is annoying. Ward flex.....no experience, I use Gas Tite only. I've ran at least a few thousand feet of the stuff and never once has there ever been an issue. Not even one little leak. You would have a really hard time finding me threading pipe. It happends but it's rare. Per manu specs, csst needs room for xpansion inspectors can go to hell. I had a guy a few years ago stand there and tell me that wasn't gas pipe and it wasn't allowed. I called him a few really foul mouthed names and very inpolitley got him off my job after I realized he was serious. That was the only time I have ever been rude to an inspector, I just have no patience for stupid people. CSST is here to stay and it's A-OK:laughing:
 

·
www.DunbarPlumbing.com
Joined
·
5,478 Posts
I don't do as much gas as some so I was wondering what what the gas gurus think about csst. Will it stand the test of time?


I only have 40' of this installed under my name, it's WardFlex back in 94 and I know the house where I installed if it blows up.


The house transferred names so I'm off the hook....not unless someone can find me.


I dislike the piping system because I've seen dogs chew through it leading to a gas water heater, I've seen it get holes rubbed through the covering and the tubing itself, I've seen people use Dawn dish detergent, only to figure out years later that chemical in the detergent slowly disintegrates the piping allowing it to leak.

It's fast and easy and I'd rather follow what I know will survive the test of time, black iron.

SCH80 metal piping takes a lot to malfunction/break/deteriorate.
 

·
Plumber Manhattan Beach
Joined
·
828 Posts
you guy's are 100% correct, no bonding to the csst. only to steel or fittings. I haven't had to bond any of my csst, seeing as I use it just for my tankless installs and I use it only under the house, I go in with steel and exit with steel, trac is never showing.

I am annoyed trying to remember who said to remove the sleeve to ground, I could have sworn that was the topic of discussion, it makes since not to ground to the csst itself as the pipe is very thin. This was a few years ago so maybe things got mixed up in the old head.

I will remember who's mouth that came out of in the middle of the night :thumbup:
 

·
Always Something
Joined
·
1,369 Posts
no bonding to the csst. only to steel or fittings.
Well, and this is just being on the anal side of things, The bond is sopposed to be on the brass fitting of the CSST, not on the steel of the meter....trunk...branch....and of course not the steel of the appliance nipple. Are inspectors down in your area requiring the bond? Or are they just happy to see a permit was pulled?

Up here, they don't have a clue about any of this sort of thing. Well, one guy does....I taught him!!

http://gastite.com/include/languages.../TB2007_01.pdf

see fig. 1http://www.contractortalk.com/showthread.php?t=34546
 

·
Certified Lunatic
Joined
·
20,658 Posts
Well, and this is just being on the anal side of things, The bond is sopposed to be on the brass fitting of the CSST, not on the steel of the meter....trunk...branch....and of course not the steel of the appliance nipple. Are inspectors down in your area requiring the bond? Or are they just happy to see a permit was pulled?

Up here, they don't have a clue about any of this sort of thing. Well, one guy does....I taught him!!

http://gastite.com/include/languages.../TB2007_01.pdf

see fig. 1
The link you posted is old and was superceded by this one.
http://www.gastite.com/include/languages/english/downloads/pdfs/TB2008_01.pdf
 

·
Always Something
Joined
·
1,369 Posts
Thanks!

Do you see the differences between the two? This whole ordeal had become and is just so lame. In my post of 06-07 TB the bond had to be made directly to the nut of the brass terminal. Someone realized that was a stupid idea and now it says it's ok to just simply bond to a portion of iron pipe. THis is one of those things that I pisses me off, in that I feel strongly in what I know to be accurate and safe, verses this stupid lawsuit enforced code addition that won't do a lick of good. But code is code and I don't make the rules.
 

·
Plumber Manhattan Beach
Joined
·
828 Posts
Well, and this is just being on the anal side of things, The bond is sopposed to be on the brass fitting of the CSST, not on the steel of the meter....trunk...branch....and of course not the steel of the appliance nipple. Are inspectors down in your area requiring the bond? Or are they just happy to see a permit was pulled?

Up here, they don't have a clue about any of this sort of thing. Well, one guy does....I taught him!!

http://gastite.com/include/languages.../TB2007_01.pdf

see fig. 1

I was tagged on a 75 gallon in Santa Monica for not bonding, even when 2 months before the place was re-piped and the inspector approved it. The repipe was done by another company. They left he 20 year old 75 gallon installed and incorrectly installed the Watts 210, so I called the inspector on it, and int he end went to his supervisor to straighten it out because I didn't want a correction, because I don't have time to go back and fix things, so they had me leave the 210 off and inspected it, well, the inspector called me on "Bonding" and the last 6" of my 1" pipe were not insulated.

The supervisors both agreed the "Approved" installation was not correct and should have failed.

So, after all the hell I went through to not get a correction notice, they gave me one anyways. I spoke to a few inspector friends of mine, one which used to be the head inspector for los angeles city, and he said it is an electrical code issue,new construction, and should have been done on the re-pipe side, if anything, not water heater change out.

They just had it out for me. Los Angeles does not require Bonding, neither does Torrance.

City of Santa Monica also requires a cross connection specialist go in and approve re-pipes. So when you pull a permit for a repipe, expect 2 seperate inspections in Santa Monica.
 

·
Always Something
Joined
·
1,369 Posts
I don't even like going to SM anymore. That place is worse that San Fransisco.
 

·
Registered
Joined
·
6 Posts
thank god i'm on the east coast

I like Trac, especially when I am installing tankless. I do agree, snak it loose in the walls and when the inspector calls you on it, fight him. Inspectors here want to see the book on it, to check for approvals and all.

I don't see any problems with it as long as it does not get hit my lightening or something. (Heard something bad about that somewhere)

electricians need to take a section of wrap off it to properly ground.

ARE YOU :censored: SERIOUS?!?!?! This is why CSST is on a temporary ban in Massachusetts right now. You never leave any stainless exposed indoor or outdoor. I was a manufacturers rep for a CSST company for 1-1/2 years. I certified over 1000 people with my product. You should be putting the bonding clamp on the first FITTING of CSST or the FITTING that is closest to the electrical panel. NEVER CONNECT THE BONDING CLAMP TO THE CSST!!! :censored: IDIOT!! Most codes in New England are saying that you (the licensed plumber and csst trained and certified) have to install the bonding clamp and run #6 grounding wire to the electrical panel, but the licensed electrician has to connect it the panel. If the black pipe system is already grounded prior to installing the CSST, then there is no need to ground the new CSST. NEVER ground to a water pipe either or secure it while running it vertical. If you ask why not, go get re-certified.:thumbsup:
 