Does (in code terms) a PRV substitute equally as replacement for a Dual Check Valve?

5560 Views 27 Replies 14 Participants Last post by  DUNBAR PLUMBING
Is it overkill to install a Pressure Reducing Valve AND and a Dual Check Valve in the same line?


Or can the Dual Check be removed, the Pressure Reducing Valve installed in place of it.


Given that some homes are required Dual Checks by authorization of local backflow prevention programs.


Is this a correct substitute.

I understand most check valves are dual, but decipher where it reasons both devices on the same line.
1 - 20 of 28 Posts
Don't they serve two distinctly different purposes? How could a PRV serve as backflow prevention or how could a DC reduce pressure?
  • Like
Reactions: 1
Is a PRV ASSE #1024? NO Your code is going to require a 1024 approved device.

There will be pressure drop over each check of a dual check valve. Maybe a total loss of 4 psi.....
Although a PRV does serve as a check valve in its operation, it acts as a single check, with in many cases an integral bypass, so it is not rated as a check valve for use in back flow prevention
Is it overkill to install a Pressure Reducing Valve AND and a Dual Check Valve in the same line?


Or can the Dual Check be removed, the Pressure Reducing Valve installed in place of it.


Given that some homes are required Dual Checks by authorization of local backflow prevention programs.


Is this a correct substitute.

I understand most check valves are dual, but decipher where it reasons both devices on the same line.
If you are installing a Reduced Pressure Principal Device at the same location as an existing dual check (way overkill) the dual check would be redundant (not needed).

Mark
If you are installing a Reduced Pressure Principal Device at the same location as an existing dual check (way overkill) the dual check would be redundant (not needed).

Mark
I read it as PRV not RPZ..
  • Like
Reactions: 2
I'm reading it as PRV and double check.........
  • Like
Reactions: 1
I read it as PRV not RPZ..
You might be right I just couldn't figure out why they would be listed together.

Mark
I'm reading it as PRV and double check.........
But how is a dual check a double check?

Mark
A double check and a dual check both have two checks...that's all I can figure. Hell, IDK if you read the post before he edited it, it made even less sense.
A dual check is non-testable. They are required by MOST municipalities. Most are in the meter loop itself.

A double check is a testable device.
  • Like
Reactions: 2
Actually a Watts L7 is testable but I still consider all dual checks disposable.

Mark
I have never seen one of those in the field. Our cross connection program does not require the annual inspection of dual checks.

Mostly see the 7.
If you want to know why a PRV ain't a BFP just open it up and take a look at the check assembly.
  • Like
Reactions: 2
I understand that never will a PRV be the suggestion of protection in backflow means,


I'm saying if I enter a home, residential service, and a customer has high water pressure.

Upon inspection I find a non-testable Wilkins 70 dual check valve assembly. Probably a requirement at the time of construction of the home.


Since I know, depending on what pressure reducing valve I install (thermal bypass not)...

is it mandatory to leave that dual check in, install the pressure reducing valve and now have 3 types of components (technically speaking) working as a check valve in that main line.

I have a customer that in order to put in the pressure reducing valve along with gauges to measure incoming and outgoing, the dual check valve's elimination makes easy work of the task.

If no, then I have to build a myriad of piping that allows to work in such a small confined area, and it will be time consuming.

I'm all about doing it right, to code...but where this home is located, they didn't even require thermal expansion protection when the dual check was installed, which can create all kinds of issues above 60psi and 120 degree water from a heating device.

This would not be inspected, and rarely do I see the requirement for dual checks on residential applications, only commercial where slight degree hazard applies.

So....it was an overkill design, even though I truly agree it is warranted, given back at the time where there were no anti-siphon hose bibbs to speak of.

At least they was thinking ahead of the game, and the neighborhood would be of the possibility where sprinkler systems would be a possibility.

That usually dictates with income levels and housing costs usually.
See less See more
:cry: this poll is flawed :cry:


im not voting,,,:laughing:
  • Like
Reactions: 1
Actually a Watts L7 is testable but I still consider all dual checks disposable.

Mark

Chicago will not recognize that as a certifiable device because it lacks a port to isolate one check from the other for testing on both the inlet and outlet side.

As for the question in the poll, a PRV is not a backflow preventer, and can't be used as such, so it would really depend on what the local code is looking for as protection to the cities water main.
I suspect Dunby that you is gonna have to hack up the piping and get em both in the line. I sure do like the meter/bfp combo but only the new houses get them.
And I don't mind doing it that way...because I'll make more money as a result. I am going to replace that dual check with a new one while we are at it. Springs always break on them, or the rubbers wear out and the clanging begins when the water gets turned off and on.
A dual check is non-testable. They are required by MOST municipalities. Most are in the meter loop itself.

A double check is a testable device.

True Matt, in backflow class we were taught that RPZ's and DC's are required to be able to be tested and re-certified 'in-line'. Repaired also as you state. That is also why devices cannot be sold w/o (2) ball valves. Must be ball valves, not gates anymore.