So you want to figure what size pump you need based on how many fixtures the pump will be handling?
Thanks bud. I thought it was 2 DFUs for each GPM I wonder why this wouldn't be in the Our code book?knuckles said:This is from the UPC not IPC but may help 710.5 Building drains or building sewers receiving discharge from any pump or ejector shall be adequately sized to prevent overloading. Two (2) fixture units shall be allowed for each gallon per minute (3.78 Lim) of flow.
Thanks! That's 709.3 in the. Michigan code also. I Appreciate you finding that.Ghostmaker said:709.3 Values for continuous and semicontinuous flow. Drainage fixture unit values for continuous and semicontinuous flow into a drainage system shall be computed on the basis that 1 gpm ( 0.06 L/s) of flow is equivalent to two fixture units. From IPC
If you found anything let me know. I just failed my residential plumbing test because I didn't know how to calculate for it.I need help sizing a sewage pump DFUs? Michigan Plumbing Code which is basically IPC its not in our code book as far as I can see. I know it's based on GPM but looking for a refresher. Thanks.
9 years later……………….If you found anything let me know. I just failed my residential plumbing test because I didn't know how to calculate for it.