Is this a problem? I don't see anything in the ipc that says cold water lines must be insulated in a building. It does mention about protection of lines from freezing but nothing but inside a building.
 

·
Professional Bullshioter
Joined
·
6,092 Posts
We have everything insulated. It's always required anywhere we work. I believe it's part of a quality installation.
 

·
Registered
Joined
·
9 Posts
Any commercial work in Illinois you can expect to insulate everything except the dwv piping. Even the horizontal runs on storm lines require insulation.
 

·
Registered
Joined
·
3 Posts
Here in florida domestic water insulation is determined by the architect. Some jobs we must do the hot and cold, some just the hot, some none at all. Down here it is a waste of money to insulate the cold water lines. I have never heard or seen one condensate in florida.
 

·
Registered
Joined
·
57 Posts
Yesterday for the 1st time ever I had a call in regards to a project we did. We ran a roof drain with overflow system, horizontally about 30 feet in ABS plastic material above a tee bar ceiling in a strip center. The contractor told me that during the rain it is dry, then a couple of days later it's dripping wet, while the overflow system is dry inside and out. It has been colder than usual, but we have numerous installations similar to this one with no problems, at least they don't call. I guess we will be insulating this one, normally we only insulate the first 8 feet inlet and outlet to water heaters, and all hot piping when a circulating system is installed.
 