Count me in as one that has done it the same way as you for 15 years. Guess could charge more and throw in another valve before that drip leg, but then they'd want a drip leg before that valve ... lol, a whole system of valves and drip legs, no need to bust out the threader.
chonkie is offline   Reply With Quote

Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. PlumbingZone.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Sponsored Links
Advertisement
 
Old 11-21-2017, 09:16 AM   #12
Senior Member
 
89plumbum's Avatar
 
Join Date: May 2011
Location: NC
Posts: 1,795

View 89plumbum's Photo Album My Photos
Default

Quote:
Originally Posted by panther View Post
I'm tripping. Wasn't the point of having drip leg after shut off valve so the drip leg could be serviced with shutting the entire house down? I mean, I'm gonna do what I have to to pass inspection. I'm just trying to figure out the logic to the new way. Seems like the way I've been doing it works perfect.
Was this in Mecklenburg? Just last week John Freeman was telling me he wanted the valve before the drip leg for the reasons you mentioned. Itís seems like their not all on the same page over there?

Also, he wants the drip leg before the regulator.
89plumbum is offline   Reply With Quote
Old 11-21-2017, 10:49 AM   #13
Senior Member
 
Join Date: Oct 2010
Posts: 110

View panther's Photo Album My Photos
Default

Quote:
Originally Posted by 89plumbum View Post
Was this in Mecklenburg? Just last week John Freeman was telling me he wanted the valve before the drip leg for the reasons you mentioned. Itís seems like their not all on the same page over there?

Also, he wants the drip leg before the regulator.
Sacramento, California.
panther is offline   Reply With Quote
Sponsored Links
Advertisement
 
Old 11-21-2017, 12:19 PM   #14
Senior Member
 
89plumbum's Avatar
 
Join Date: May 2011
Location: NC
Posts: 1,795

View 89plumbum's Photo Album My Photos
Default

My bad man, I was thinking of Pathmaker who lives near me.
89plumbum is offline   Reply With Quote
Old 11-21-2017, 04:47 PM   #15
GAN
Super Moderator
 
GAN's Avatar
 
Join Date: Jul 2012
Location: St. Louis Metro
Posts: 2,069

View GAN's Photo Album My Photos
Default

Hmm illustration right out of the IFGC 2012 edition.

DRIP. The container placed at a low point in a system of piping
to collect condensate and from which the condensate is
removable.

These reservoirs, also referred to as “drip legs,” are
made up of pipe and fittings and are intended to collect
liquid in piping systems where condensables are
possible. A “drip leg” is distinct from a “sediment trap”
even though they may be constructed identically.

408.4 Sediment trap. Where a sediment trap is not incorporated
as part of the appliance, a sediment trap shall beinstalled downstream of the appliance shutoff valve as close to the inlet of the appliance as practical. The sediment trap shall be either a tee fitting having a capped nipple of any length installed vertically in the bottommost opening of the
tee as illustrated in Figure 408.4 or other device approved as an effective sediment trap. Illuminating appliances, ranges, clothes dryers, decorative vented appliances for installation in vented fireplaces, gas fireplaces, and outdoor grills need not be so equipped.

 In addition to the code requirement, most appliance manufacturers require the installation of a sediment trap (dirt leg) to protect the appliance from debris in the gas. Note that a drip leg is not the same as a sediment trap (see Section 408.2). Sediment traps are necessary to protect appliance gas controls from the dirt, soil, pipe chips, pipe joint tapes and compounds and construction site debris that enter the piping during storage, handling, installation and repairs. Hazardous
appliance operation could result from foreign matter entering gas controls and burners. Despite the fact that utilities supply clean gas, foreign matter can enter the piping prior to and during installation both
on the utility side of the system and on the customer
side.

Sediment traps are designed to cause the gas flow to change direction 90 degrees (1.57 rad) at the sediment collection point, thus causing the solid or liquid contaminants to drop out of the gas flow [see Commentary
Figure 408.4(1)]. The nipple and cap should not be placed in the branch opening of a tee fitting because this would not create a change in direction of flow and would allow debris to simply pass/jump over the capped nipple collection point. Commentary Figure 408.4(2) illustrates a relatively ineffective sediment trap, however, such configurations are not
expressly prohibited by the wording of this section. The text speaks of the bottommost opening of the tee without prohibiting such opening from being the branch opening. Note that Code Figure 408.4 illustrates
the intent to have the nipple and cap in the run of the tee, thereby suggesting that it is not the intent to have it in the branch of the tee. The code does not specify a minimum length for the capped nipple,
therefore, it could be from a close nipple on up. Three to 6 inches is the customary length. The capped nipple must be in a vertical plane to allow the sediments to fall in by gravity. The sediment trap must be as close to the appliance inlet as practical to be able to capture sediment from all of the piping upstream of the appliance connection. The sediment trap must be downstream of the appliance shutoff valve to allow the trap to be serviced after closing the upstream shutoff valve. Manufactured sediment traps are available that have the configuration of a straight section of pipe and are equipped with cleanout openings. Although it would be wise to install sediment traps at all appliance connections, they are not mandated by code for gas lights, ranges, clothes dryers and outdoor grills. These appliances are also susceptible to harm from debris in gas, especially ranges and clothes dryers, and the appliance manufacturer may require sediment traps where the code does not. The
code’s logic is that these exempt appliances are manually operated rather than automatically operated; therefore, the user would be in attendance and aware of a problem.
Attached Images
  
__________________
Il. Lic.# 058-106725, Il. C.C.D.I. Lic. # XCO396
Remember valor, honor, independence, family & clan;
I do whenever I hear the ceol mor,
the "great music" of the Highland bagpipe. I swear upon the holy iron of my dirk that I will not forget.
GAN is offline   Reply With Quote
The Following 5 Users Say Thank You to GAN For This Useful Post:
breplum (11-22-2017), Debo22 (11-21-2017), MACPLUMB777 (11-21-2017), slumplumber (11-22-2017), Tommy plumber (11-21-2017)
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Dark flakes in water - tankless water heater bt5000 General Plumbing Discussion 14 04-01-2016 12:23 PM
Question about water supply for tankless heater GrtLksPlbr General Plumbing Discussion 27 12-01-2015 11:59 AM


All times are GMT -4. The time now is 09:34 AM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2020, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.1
vBulletin Security provided by vBSecurity v2.2.2 (Pro) - vBulletin Mods & Addons Copyright © 2020 DragonByte Technologies Ltd.
User Alert System provided by Advanced User Tagging (Pro) - vBulletin Mods & Addons Copyright © 2020 DragonByte Technologies Ltd.
Our Pro Sites Network
ContractorTalk.com | DrywallTalk.com | ElectricianTalk.com | HVACSite.com | PaintTalk.com | RoofingTalk.com