Originally Posted by OpenSights View Post
Update. Had a couple inspections yesterday with inspector B and asked him about this issue. Apparently thereís a code in the mechanical code book thatís not in the plumbing code book. Because of the size of the chimney, 8x12 I think he said, it is oversized for the btuís of the furnace and heater. Somehow the 4/3Ē vent fcks with the math and needs to be a 4Ē not tapered down to 3Ē.

Iím not a HVAC tech, understand very little of the trade and code. In plumbing and drain cleaning, there are many codes I agree with, but some I think are totally unnecessary and only there for permit revenue.
Good point. Yes when an old chimney is oversized with more efficient devices which run cooler. Heat equals convection & velocity, less heat convection & velocity. Mostly though it works in reverse. Smaller diameter piping less heat and velocity loss.

For instance, 100,00 total BTU may be fine in a single story structure with an 8" flue, not much chance for loss. Now a 2 story structure with an 8" flue, to much heat and velocity loss. Convection stops and vent gases pour back into and around a bonnet. Reduce the size of the flue to 6" and the heat loss and velocity are not affected. Been a while since I've sat and done the math. Have seen it happen when people go from a 40% efficient furnace with a brick chimney to an 80% connected to the same brick chimney. You have to use the old chimney as a liner for a metal B vent.
__________________
Il. Lic.# 058-106725, Il. C.C.D.I. Lic. # XCO396
Remember valor, honor, independence, family & clan;
I do whenever I hear the ceol mor,
the "great music" of the Highland bagpipe. I swear upon the holy iron of my dirk that I will not forget.
GAN is offline   Reply With Quote

Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. PlumbingZone.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Sponsored Links
Advertisement
 
Old 04-19-2019, 05:00 PM   #32
Super Moderator
 
OpenSights's Avatar
 
Join Date: Mar 2015
Location: Grand Ledge, MI
Posts: 4,612

View OpenSights's Photo Album My Photos
Default

Quote:
Originally Posted by GAN View Post
Good point. Yes when an old chimney is oversized with more efficient devices which run cooler. Heat equals convection & velocity, less heat convection & velocity. Mostly though it works in reverse. Smaller diameter piping less heat and velocity loss.

For instance, 100,00 total BTU may be fine in a single story structure with an 8" flue, not much chance for loss. Now a 2 story structure with an 8" flue, to much heat and velocity loss. Convection stops and vent gases pour back into and around a bonnet. Reduce the size of the flue to 6" and the heat loss and velocity are not affected. Been a while since I've sat and done the math. Have seen it happen when people go from a 40% efficient furnace with a brick chimney to an 80% connected to the same brick chimney. You have to use the old chimney as a liner for a metal B vent.

Question, out of curiosity, does outside conditions, factor in? He checked the draw, as we always do and it was drawing perfectly. He uses dust, we use a lighter. Single story house. Also if both the heater and furnace fire at the same time, is that a factor?

I thought the reason for liners was due to more moisture because of the higher efficiency. You donít want moisture getting into the nicks and cracks during winter. Expansion contraction. Not draw...

I guess itís similar to drainage. When I see a kitchen line only on a 4Ē underground 50% of the time a jetter is needed. I always give the customer the option of me attempting, but they have to pay either way. Itís rare I see it, maybe once every couple of years.
skoronesa likes this.
OpenSights is offline   Reply With Quote
Old 04-29-2019, 11:47 AM   #33
GAN
Super Moderator
 
GAN's Avatar
 
Join Date: Jul 2012
Location: St. Louis Metro
Posts: 1,902

View GAN's Photo Album My Photos
Default

Sorry, been out on vacation.

Work harder when I am out. Glad to be back to work...…..



Yes outside conditions make a difference, but I don't believe they are addressed directly in any code. If any code did I think it would be under the IECC possible the mechanical code. I can't recall anything in the IMC.

Heater & WH firing at the same time would tend to eliminate a possible drafting issues, more heat more velocity. Less chance of vent gasses cooling & falling.


I have seen this in new construction as well with an ultra tight home and not enough combustion air being drawn in.

Yes a liner is for keeping moisture down but it is a two fold game.


Under the right conditions (seems to be more of an issue during summer) I have seen more than one WH not draft and spill out CO into the basement. I believe cooler indoor air affects what would be in the winter a natural tendency to draft upward with hotter air and vent gasses.
OpenSights and skoronesa like this.
__________________
Il. Lic.# 058-106725, Il. C.C.D.I. Lic. # XCO396
Remember valor, honor, independence, family & clan;
I do whenever I hear the ceol mor,
the "great music" of the Highland bagpipe. I swear upon the holy iron of my dirk that I will not forget.
GAN is offline   Reply With Quote
Sponsored Links
Advertisement
 
Old 04-29-2019, 12:47 PM   #34
Senior Member
 
ShtRnsdownhill's Avatar
 
Join Date: Jan 2016
Location: Long Island, NY
Posts: 4,430

View ShtRnsdownhill's Photo Album My Photos
Default

most appliances ( water heaters, boilers, furnaces, etc) have the size chimney and distance sizes in the installation booklet, with all the higher performances now its even more critical to follow them so you dont have problems...that big oil guzzler in that big chimney was no issue, till you install an efficient gas unit that exhausts less than half the heat to old one did, each job you do has to be looked at and sized to what your putting in or you will have problems..
a chimney on the exterior of the house is different than one on an inside wall, as now you have the outside climate affecting draft either by chilling or heating the chimney flue way..almost all gas appliances now should not go into an unlined brick or mortar chimney, should be lined with stainless steel liner...
different municipalities have their own add ons, but if you stick with the manufactures specs you should be good and any inspector should agree with the manufacture..
GAN, OpenSights, skoronesa and 1 others like this.
__________________
You cant cure stupid, only kill it..
ShtRnsdownhill is online now   Reply With Quote
Old 04-29-2019, 06:04 PM   #35
Super Moderator
 
OpenSights's Avatar
 
Join Date: Mar 2015
Location: Grand Ledge, MI
Posts: 4,612

View OpenSights's Photo Album My Photos
Default

Funny you bring this thread back up today. Tomorrow’s reinspection. This time we’re meeting with the mechanical inspector.

We found a true 4” vent hood and installed it last week. To be honest, I don’t understand the math behind it, but when we had the combo hood it sucked the flame of a bic lighter in nice and hard. When we put the true 4” hood it barely sucked it in at all. Weather on both days of installation and first inspection were pretty close. LL is going to install a couple carbon monoxide detectors.

With what I saw, if that were my house with my kid and wife.... the combo hood would be going back in after inspection.... if I were to actually pull a permit in my own house that is.
skoronesa and Tango like this.
OpenSights is offline   Reply With Quote
Old 04-29-2019, 06:37 PM   #36
Super Moderator
 
OpenSights's Avatar
 
Join Date: Mar 2015
Location: Grand Ledge, MI
Posts: 4,612

View OpenSights's Photo Album My Photos
Default

Quote:
Originally Posted by ShtRnsdownhill View Post
most appliances ( water heaters, boilers, furnaces, etc) have the size chimney and distance sizes in the installation booklet, with all the higher performances now its even more critical to follow them so you dont have problems...that big oil guzzler in that big chimney was no issue, till you install an efficient gas unit that exhausts less than half the heat to old one did, each job you do has to be looked at and sized to what your putting in or you will have problems..
a chimney on the exterior of the house is different than one on an inside wall, as now you have the outside climate affecting draft either by chilling or heating the chimney flue way..almost all gas appliances now should not go into an unlined brick or mortar chimney, should be lined with stainless steel liner...
different municipalities have their own add ons, but if you stick with the manufactures specs you should be good and any inspector should agree with the manufacture..
We called Rheem, talked with the rep and he said the combo vent was within manufacture specs for our situation.... but the Bible says....
skoronesa likes this.
OpenSights is offline   Reply With Quote
Old 04-29-2019, 08:20 PM   #37
Senior Member
 
ShtRnsdownhill's Avatar
 
Join Date: Jan 2016
Location: Long Island, NY
Posts: 4,430

View ShtRnsdownhill's Photo Album My Photos
Default

Quote:
Originally Posted by OpenSights View Post
Funny you bring this thread back up today. Tomorrowís reinspection. This time weíre meeting with the mechanical inspector.

We found a true 4Ē vent hood and installed it last week. To be honest, I donít understand the math behind it, but when we had the combo hood it sucked the flame of a bic lighter in nice and hard. When we put the true 4Ē hood it barely sucked it in at all. Weather on both days of installation and first inspection were pretty close. LL is going to install a couple carbon monoxide detectors.

With what I saw, if that were my house with my kid and wife.... the combo hood would be going back in after inspection.... if I were to actually pull a permit in my own house that is.

the funnel or reduction in hood created a venturi like effect, the velocity was more through a smaller hole and created a good suction that pulled the bic lighter flame, once you opened up the hood to full 4 inch you cut the velocity and created less of a suction, that is my understanding of it as learned over the years, it may not be the engineered answer...
GAN, OpenSights and skoronesa like this.
__________________
You cant cure stupid, only kill it..
ShtRnsdownhill is online now   Reply With Quote
Old 04-29-2019, 08:51 PM   #38
Super Moderator
 
OpenSights's Avatar
 
Join Date: Mar 2015
Location: Grand Ledge, MI
Posts: 4,612

View OpenSights's Photo Album My Photos
Default

Quote:
Originally Posted by ShtRnsdownhill View Post
the funnel or reduction in hood created a venturi like effect, the velocity was more through a smaller hole and created a good suction that pulled the bic lighter flame, once you opened up the hood to full 4 inch you cut the velocity and created less of a suction, that is my understanding of it as learned over the years, it may not be the engineered answer...
Exactly my understanding too!

Tomorrow I hope we get an education. I know the mechanical inspector, but he probably doesnít remember me. I use to cable his main line as a prevent. I like the guy, no dummy like my plumbing inspectors.

I only know plumbing mechanical vent code, not actual mechanical vent code.
OpenSights is offline   Reply With Quote
Old 04-30-2019, 07:13 PM   #39
Super Moderator
 
OpenSights's Avatar
 
Join Date: Mar 2015
Location: Grand Ledge, MI
Posts: 4,612

View OpenSights's Photo Album My Photos
Default

So inspector A showed up instead of the mechanical inspector. Both my Master an I were pissed! Got a sticker, so LL was happy. We had all kinds of questions ready for the mechanical inspector ready. My plumbing inspector A can’t explain the code.... it’s just in the book. In reality, his job isn’t about following code, his job is a revenue generator. That is a fact straight from plumbing inspector B’s mouth. If they don’t get x amount of reinspection fees they don’t have a job.
OpenSights is offline   Reply With Quote
Old 05-07-2019, 08:50 PM   #40
Senior Member
 
czplumbing's Avatar
 
Join Date: Nov 2014
Location: East Hampton NY
Posts: 122

View czplumbing's Photo Album My Photos
Default

Quote:
Originally Posted by OpenSights View Post
You donít have inspectors??!!?!! Really? The official who determines if the plumbing work was performed in compliance with the health and safety of the nation... they donít inspect?

Only thing they inspect around here is rough plumbing when we are doing a new house or reno. They only inspect the PVC : So your telling me to even install a water heater you need an inspector to check it out to make sure it was installed right ?
czplumbing is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Gas line at water heater fiddler General Plumbing Discussion 21 10-10-2018 10:30 AM
Two failed water heater inspections drip leg panther Plumbing Code 14 11-21-2017 04:47 PM
Think I got someone fired friday.... Master Mark General Plumbing Discussion 10 09-25-2017 05:32 PM
Dark flakes in water - tankless water heater bt5000 General Plumbing Discussion 14 04-01-2016 12:23 PM


All times are GMT -4. The time now is 01:05 PM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.1
vBulletin Security provided by vBSecurity v2.2.2 (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
User Alert System provided by Advanced User Tagging (Pro) - vBulletin Mods & Addons Copyright © 2019 DragonByte Technologies Ltd.
Our Pro Sites Network
ContractorTalk.com | DrywallTalk.com | ElectricianTalk.com | HVACSite.com | PaintTalk.com | RoofingTalk.com