Quote:
Originally Posted by younger-plumber View Post
haha. im just tryin to get some ideas on ways to make sales. aka ma'am i would reccomend putting in this expansion tank when we install your prv. just as a safety precaution.to ease both of our minds in the future of any problems that may occur. haha
Most towns in the Seattle area require an expansion tank on all water heaters. But all areas require an expansion tank with any type or style of closing a system PRV DC RPBP whatever. To many problems with high pressure here I have seen 215psi on city lines. UPC Code requires we allow for thermal expansion but most localities add there bit to it.
PlumberDave is offline   Reply With Quote
Join Contractor Talk

Join the #1 Plumbers Forum Today - It's Totally Free!

PlumbingZone.com - Are you a Professional Plumbing Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for plumbers to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that PlumbingZone.com is a great community to join. Best of all it's totally free!

Join PlumbingZone.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. PlumbingZone.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!
Old 03-03-2010, 01:01 AM   #12
Always Something
 
Tankless's Avatar
 
Join Date: Jun 2008
Location: Santa Barbara / Ventura
Posts: 1,347

View Tankless's Photo Album My Photos
Default

Intersesting enough....and I made a comment on the recent threads about this topic. I had a job where I was walking the inspector through everything. Out at the street there is an RPZ on 1" risers. At the house service entrance, there is 1". There is also 1 1/4" for (what I assumed) suppression. Inspector told me the RP was for fire. I showed him the piping and its sizes and he scratched his head. Said "looks like a goof". I just told him there is an XTX on the domestic. I get him to the location of my tankless heaters and he said I didn't need the XTX. Never gave me a good reason for it, just told me with the setup I had it was overkill but he said he likes that I airred on the side of safety. I just told him, I found what I thought was a closed system, therefor without further question it gets an XTX. He said....."yeah...but with the tankless it's just not necessary." I didn't really know what else to say.
__________________
"It's now. You just go for it now and you worry about the future and the past later." -Steve Nash

And when I leave come together like butt cheeks
-Grits n Gravy
Tankless is offline   Reply With Quote
Old 03-03-2010, 01:06 AM   #13
Cruise Director
 
ToUtahNow's Avatar
 
Join Date: Jul 2008
Location: California/Nevada/Utah
Posts: 2,414

View ToUtahNow's Photo Album My Photos
Default

Quote:
Originally Posted by Tankless View Post
Intersesting enough....and I made a comment on the recent threads about this topic. I had a job where I was walking the inspector through everything. Out at the street there is an RPZ on 1" risers. At the house service entrance, there is 1". There is also 1 1/4" for (what I assumed) suppression. Inspector told me the RP was for fire. I showed him the piping and its sizes and he scratched his head. Said "looks like a goof". I just told him there is an XTX on the domestic. I get him to the location of my tankless heaters and he said I didn't need the XTX. Never gave me a good reason for it, just told me with the setup I had it was overkill but he said he likes that I airred on the side of safety. I just told him, I found what I thought was a closed system, therefor without further question it gets an XTX. He said....."yeah...but with the tankless it's just not necessary." I didn't really know what else to say.
I believe it is only hot water storage they are concerned with. In theory, the system is open when a tankless fires.

Mark
ToUtahNow is offline   Reply With Quote
The Following 5 Users Say Thank You to ToUtahNow For This Useful Post:
Plumbworker (03-06-2010), Protech (03-06-2010), Redwood (03-06-2010), robthaplumber (03-04-2010), Tankless (03-07-2010)
Old 03-04-2010, 11:51 PM   #14
2nd Generation Plumber
 
robthaplumber's Avatar
 
Join Date: Jan 2010
Location: Nashville TN.
Posts: 149

View robthaplumber's Photo Album My Photos
Default

Go ahead and install an expansion tank. It will prevent a call back. I have installed prv's with integral bypasses and still had to install a XTank. Save yourself a trip back and put one in.
__________________
Good Plumb'n aint cheap, Cheap Plumb'n aint Good
robthaplumber is offline   Reply With Quote
The Following 4 Users Say Thank You to robthaplumber For This Useful Post:
Airgap (03-06-2010), Plumbworker (03-06-2010), Redwood (03-06-2010), service guy (03-06-2010)
Old 03-05-2010, 12:05 AM   #15
Senior Member
 
AKdaplumba's Avatar
 
Join Date: Jan 2010
Location: Vancouver BC
Posts: 726

View AKdaplumba's Photo Album My Photos
Default

is the bypass intergrated within the PRV? I have never noticed one on any that we have installed.
AKdaplumba is offline   Reply With Quote
Old 03-06-2010, 01:32 AM   #16
2nd Generation Plumber
 
robthaplumber's Avatar
 
Join Date: Jan 2010
Location: Nashville TN.
Posts: 149

View robthaplumber's Photo Album My Photos
Default

According to the manufacturer, yes. Check out the Watts website.
__________________
Good Plumb'n aint cheap, Cheap Plumb'n aint Good
robthaplumber is offline   Reply With Quote
Old 03-06-2010, 03:26 PM   #17
jA-Rod dat u?
 
Redwood's Avatar
 
Join Date: Sep 2008
Location: Connecticut
Posts: 9,252

View Redwood's Photo Album My Photos
Default

Some PRV's have an integral bypass while others don't.

Truth be told the bypass is only effective if the water supply pressure is low enough to absorb the pressure caused by thermal expansion without getting close enough to 150-psi to activate the T&P valve.

One thing you should consider with water heaters is they are pressure vessels and there is a certain amount of expansion and contraction from pressure changes built into the design.

If your installation of an internal bypass PRV without a thermal expansion tank is allowing the pressure to cycle from the set pressure of the PRV @ 75-psi up to 145-psi on thermal expansion where it matches the 145-psi line pressure in the street and it bypasses through the PRV without the T&P activating, even though there are no symptoms that would generate a callback, you aren't doing your customer any favors.

Similar to the nine lives of a cat each pressure cycle from 75-psi up to 145-psi and back down has an effect on the service life of the water heater. The glass lining will crack allowing water to reach the steel and start the corrosion process, and the steel tank itself will start to experience metal fatigue from the flexing during the cycles. Simply stated the tank will start to leak much sooner than a tank which is at a constant pressure.

Even if the water supply pressure is in the lower ranges such as 90-psi and you install a PRV with an internal bypass your installation is only good as long as the water company doesn't come and install a new meter and check valve or, increase the water supply pressure to cover the water supply needs of that new development up on the hill.

Metal fatigue from pressure cycling is real and the illustration I commonly use is Aloha Airlines Flight 243 where an Boeing 737-297 airliner was used it's whole life in service on short hops island to island in Hawaii. In doing so it racked up a huge number of pressure cycles despite having a low number of hours on the airframe. The aircraft had the second highest number of cycles at 89,090 in the entire 737 fleet, the airframe had only 35,496 hours in flight, the Boeing design was expected to be good for 51,000 hours and 75,000 cycles. However due to many of the flights not going high enough to require full pressurization not all the cycles were counted in accordance with the methods used at that time, Flight 243 changed that! The aircraft was at 24,000 feet in flight when the skin of the aircraft failed and they had an explosive decompression. http://www.aloha.net/~icarus/index.htm

Do yourself and your customer a favor and install an expansion tank!
I would consider it good plumbing.
__________________
"Fascism should rightly be called Corporatism, as it is the merger of corporate and government power."
~Benito Mussolini~
Lloyd Blankfein for President 2012 - Save Money Cut Out The Middleman!
Redwood is offline   Reply With Quote
The Following 5 Users Say Thank You to Redwood For This Useful Post:
Airgap (03-06-2010), gusty60 (03-07-2010), Protech (03-06-2010), robthaplumber (03-06-2010), service guy (03-06-2010)
Old 03-06-2010, 10:40 PM   #18
٩(͡๏̯͡๏)۶
 
Protech's Avatar
 
Join Date: Sep 2008
Location: Polk County, Florida
Posts: 7,167

View Protech's Photo Album My Photos
Send a message via Skype™ to Protech
Default

Well said, Red

Quote:
Originally Posted by Redwood View Post
Some PRV's have an integral bypass while others don't.

Truth be told the bypass is only effective if the water supply pressure is low enough to absorb the pressure caused by thermal expansion without getting close enough to 150-psi to activate the T&P valve.

One thing you should consider with water heaters is they are pressure vessels and there is a certain amount of expansion and contraction from pressure changes built into the design.

If your installation of an internal bypass PRV without a thermal expansion tank is allowing the pressure to cycle from the set pressure of the PRV @ 75-psi up to 145-psi on thermal expansion where it matches the 145-psi line pressure in the street and it bypasses through the PRV without the T&P activating, even though there are no symptoms that would generate a callback, you aren't doing your customer any favors.

Similar to the nine lives of a cat each pressure cycle from 75-psi up to 145-psi and back down has an effect on the service life of the water heater. The glass lining will crack allowing water to reach the steel and start the corrosion process, and the steel tank itself will start to experience metal fatigue from the flexing during the cycles. Simply stated the tank will start to leak much sooner than a tank which is at a constant pressure.

Even if the water supply pressure is in the lower ranges such as 90-psi and you install a PRV with an internal bypass your installation is only good as long as the water company doesn't come and install a new meter and check valve or, increase the water supply pressure to cover the water supply needs of that new development up on the hill.

Metal fatigue from pressure cycling is real and the illustration I commonly use is Aloha Airlines Flight 243 where an Boeing 737-297 airliner was used it's whole life in service on short hops island to island in Hawaii. In doing so it racked up a huge number of pressure cycles despite having a low number of hours on the airframe. The aircraft had the second highest number of cycles at 89,090 in the entire 737 fleet, the airframe had only 35,496 hours in flight, the Boeing design was expected to be good for 51,000 hours and 75,000 cycles. However due to many of the flights not going high enough to require full pressurization not all the cycles were counted in accordance with the methods used at that time, Flight 243 changed that! The aircraft was at 24,000 feet in flight when the skin of the aircraft failed and they had an explosive decompression. http://www.aloha.net/~icarus/index.htm

Do yourself and your customer a favor and install an expansion tank!
I would consider it good plumbing.
Protech is offline   Reply With Quote
The Following User Says Thank You to Protech For This Useful Post:
Redwood (03-06-2010)
Old 03-07-2010, 12:02 PM   #19
Senior Member
 
Join Date: Jul 2008
Posts: 392

View grandpa's Photo Album My Photos
Default

Even with a bypass on the regulator, the pressure on the house side could increase up to the point where it equals street pressure. Remember that at 150 PSI the relief valve should be wide open. In my experience, a relief valve may start to "weep" at pressures as low as 120 or so. The expansion tank is the only way to avoid that.
grandpa is offline   Reply With Quote
Old 03-07-2010, 07:01 PM   #20
Cruise Director
 
ToUtahNow's Avatar
 
Join Date: Jul 2008
Location: California/Nevada/Utah
Posts: 2,414

View ToUtahNow's Photo Album My Photos
Default

There's no question you need to know the historic highs and lows of a system. I am on a tank so my pressure is constantly 185 psi and would need an expansion tank. Up the hill and across the highway they have 35 psi from the same tank. Now if I go into Westwood they are on a reservoir and depending on the water level at the time they vary between 85 psi and 150 psi so I would install an expansion tank.

Mark
ToUtahNow is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Correct me if I am wrong but Bollinger plumber Off Topic 22 11-07-2009 05:53 PM
please help correct my plumbing/vents drawing Nittaya General Plumbing Discussion 4 10-23-2009 10:28 AM
Is it wrong DUNBAR PLUMBING Business, Marketing, and Sales 8 10-15-2009 12:52 PM
What's wrong here ESPinc Plumbing Pictures 12 10-11-2009 01:25 AM
What's wrong here... Airgap Plumbing Pictures 18 07-20-2009 11:57 PM


Top of Page | View New Posts

All times are GMT -4. The time now is 07:16 AM.


Powered by vBulletin® Version 3.8.6
Copyright ©2000 - 2012, Jelsoft Enterprises Ltd.
Search Engine Optimization by vBSEO 3.6.0 RC 2
Plumbing Zone © 2010The Building Network LLC