Buderus GB142 Problems - Plumbing Zone - Professional Plumbers Forum
Old 04-03-2010, 11:00 AM   #1
View OldSchool's Photo Album My Photos
Default Buderus GB142 Problems
Here are a few of the problems with these units I have come across.
1. Circulating pump on low loss heater defect not working.
2. Condensation from bottom outlet full of corrosion only after 1 year.
3. Condensate trap plugging up with corrosion.
4. control board will not run on back up generator.....
5. Can not install large pump on boiler control it blows the internal fuse
OldSchool is offline   Reply With Quote
Old 04-04-2010, 11:54 AM   #2
View Scott K's Photo Album My Photos
Regarding #2 & #3
Well I'm assuming because you're in Ontario that the GB142's that you come accross work a bit harder then the ones I know of out here in Vancouver. These boilers DO need to be cleaned once or twice a year depending on how hard they worked and that involves the mineral oil trick.
Because they are an aluminum heat exchanger they oxidize overtime due to the corrossive condensate and some of this oxidation & little metal pieces sinks into the condensate trap and obviously plugs it if not taken care of regularly.
Having said that I'm not a fan of them personally because of the aluminum heat exchanger. I like the stainless steel ones myself personally. But despite this aluminum heat exchanger, I know of a few guys that think the world of these boilers and a friend of mine has one in his house that hasn't given him any problems in 2 1/2 years of operation and we cleaned it once and it wasn't that bad.
Scott K is offline   Reply With Quote
Old 04-05-2010, 12:53 AM   #3
njoy plumbing's Avatar
View njoy plumbing's Photo Album My Photos
Have never installed buderus before. I agree with Scott K, that alum x chgrs need to be serviced more often. I also install only stainless. That said, I service lots of alum boilers and they work fine.
Trangle Tube or IBC
njoy plumbing is offline   Reply With Quote
Old 04-05-2010, 06:38 AM   #4
View trick1's Photo Album My Photos
There are only a few instances where I've run into a clogged condensate line.
1) The unit isn't getting yearly service.
2) sometimes the intake air is full of particulate which creates a problem after combustion, usually scale forming on the exchanger, some of which ends up clogging the condensate line.
I haven't had too many problems with the GB otherwise. I've only installed a couple but I service a few.
I've been sticking with the Utica UB95 lately since I can forgo the primary/secondary in a lot of instances.
trick1 is offline   Reply With Quote
The Following User Says Thank You to trick1 For This Useful Post:
Plumbworker (10-26-2012)
Old 10-26-2012, 10:20 AM   #5
View lighthouseplumb's Photo Album My Photos
1. Circulating pump on low loss heater defect not working, this is not a Answer: Buderus issue, it is a installer issue.
2. Condensation from bottom outlet full of corrosion only after 1 year,
Answer: If you follow instructions on installation you will learn that this is another poor installer issue, you are required to perform a water quality check prior to installation..
3. Condensate trap plugging up with corrosion,
Answer: This is another poor installer issue, is there a sediment trap on the gas piping.
4. Will not run on back up generator.....Answer: No high tech boiler or computer will run on a cheap Home Depot generators, cheap generators produce a square wave, normal power and whole house generators produce a sine wave, if you have a cheap generator you must install a inverter.
Answer: Again this is poor installation, you are not suppose to install a large circulatior on this boiler, you are required to install a relay panel.. Read the boiler manufacturing instructions..get educated.
lighthouseplumb is offline   Reply With Quote
Old 10-26-2012, 10:22 AM   #6
I am a train Buderus installer and Tech. Obviously the person posting these answers is not, If he read the manual he would have realized every one of these post where installer error.
Old 10-26-2012, 10:54 AM   #7
The Token Engineer
ZL700's Avatar
View ZL700's Photo Album My Photos
Wink
How do you read when you can barely write?
If fire is involved, I LIKE IT!
ZL700 is offline   Reply With Quote
The Following User Says Thank You to ZL700 For This Useful Post:
rjbphd (10-26-2012)
Old 10-26-2012, 11:00 AM   #8
Who let you in without posting a required intro???
Old 10-26-2012, 11:02 AM   #9
The cir pump was a s25 Armstrong ... That blew the fuse ... I don't think amp draw on that is to much ....
Change to a direct drive and it was fine ...
We do 3 to 4 gb142 a week ...
I think I have a hell of a lot more experience on these units
Old 10-26-2012, 11:05 AM   #10
Generators make sine wave not square wave ... Now go educate yourself ...
The issue was the frequency ... And you though you knew what you were talking about
The Following User Says Thank You to OldSchool For This Useful Post:
Gettinit (10-26-2012)
Problems with toilets. user2090 General Plumbing Discussion 11 02-17-2010 10:43 PM
Jet Well Pump Problems dannyjoe Residential Plumbing 2 09-26-2009 05:47 PM
Well Pump problems 3KP General Plumbing Discussion 9 05-27-2009 10:35 PM
BTN-200 Problems KratzerPlumbing General Plumbing Discussion 6 05-03-2009 08:35 PM
Elbow Problems DUNBAR PLUMBING Off Topic (Non Trade) 6 11-30-2008 11:57 AM